Fuses and disconnect

Status
Not open for further replies.

rich1956

Member
We have a device that has 18 outputs that operate at 95 VDC with a max current of 10 amps to drive fuel solenoids on an engine in a Class I Div 2 Group D location. I need to protect each output circuit and associated wiring. We would like to use a high speed ceramic fuse for each circuit and use the device disconnect switch as a means to shut off power in order to service the fuses. Article 501.105 (B)(5) states each fuse needs a disconnect switch - we would like to use the one device disconnect for all fuses. Does that design approach satisfy the requirements?

Thanks for any and all opinions.

Rich
 

john m. caloggero

Senior Member
Re: Fuses and disconnect

Section 501.105(B) of the 2005 NEC does not require a disconnect for fuses. Part IV of Article 240, section 240.40 requires fuses in circuits greater than 150 volts to have a disconnecting means, however, cartridge fuses of any voltage where accessible to other than qualified persons require a disconnecting means.
 