fuses and incident energy
billsnuff
can someone explain the differences between
FRS-R xxx
KTS-R xxx
LPS-RK_SPI XXX
in regards to an industrial environment (re:arc flash, motor starting and minimizing fuse inventory)?
Thanks
jim dungar
Wisconsin
PE (Retired) - Power Systems
There is no one 'great for every application' fuse. Bussmann like to push their LPS-RK offering as a universal replacement.
In all of the arc flash studies I have performed, I have rarely recommended replacing existing FRS-R fuses with LPS-RK. I find that most branch circuits do not have enough arcing fault current to cause the fuse to enter its current limiting range. There have even been more cases where I suggested replacing LPS-RK fuses with FRS-R ones.
billsnuff
Pierre,
thanks for the reply. I am using FRS-R dual element time delay in most all cases. In order to lower IE, KTS-R single element current limiting are being recommended. I am trying to decide if LPS-RK dual element, time delay, current limiting is a better choice in most or all cases. Was hoping someone else had some experience to share.
jim dungar
Wisconsin
Pierre,
I do not think I would disagree with using KTS-R, especially for fuses smaller than 200A.
billsnuff
thanks jim,
so i guess i keep the dual inventory FSR-R and KTS-R and skip the other,
unless recommended for a specific application.
actually ran across the low peak fuses as they were sent as an equilivent for one of the others, another one of the many reasons for asking for the input.
MH.com scores again :cool:
P>S> the closest i got to being an engineer was playing with my wind up train.:grin: