I have a motor control package that is a 3phase 460volt motor contactor w/overloads and currently we are fusing 2 wires for controls. The fuses that we are using are 600v/700v rated. My question is: Can we use either a breaker, resetable fuses, or even fuses themselves that are rated at 300 volt?
The ampacity of these controls is 2 amp fuses, but the FLC is less than that... We are trying to improve the overall control package for these motors, but the catch to using all 300 volt fuses is the 3ph 460v motors that we send out. Remember that the two phases will be only 277v to ground. And I did read 240.60(1) in the 2008 NEC that states that I cannot, due to the phase-to-phase voltage is over 300v. 240.60(2) states though a single phase that is fed from a 3ph 4 wire is acceptable if the phase-to-neutral is less than 300v. But I have no neutral at any of these motors that we sell. These are 50" fans, and the power to the control package is done by qualified electricians in the field all over the world. The control package is self contained at the bottom of the fan, and the only things these fuses actually run are a fractional oscillating motor and the motor contactor COIL ONLY! Thank you for your time to review and answer my question.
Randy
The ampacity of these controls is 2 amp fuses, but the FLC is less than that... We are trying to improve the overall control package for these motors, but the catch to using all 300 volt fuses is the 3ph 460v motors that we send out. Remember that the two phases will be only 277v to ground. And I did read 240.60(1) in the 2008 NEC that states that I cannot, due to the phase-to-phase voltage is over 300v. 240.60(2) states though a single phase that is fed from a 3ph 4 wire is acceptable if the phase-to-neutral is less than 300v. But I have no neutral at any of these motors that we sell. These are 50" fans, and the power to the control package is done by qualified electricians in the field all over the world. The control package is self contained at the bottom of the fan, and the only things these fuses actually run are a fractional oscillating motor and the motor contactor COIL ONLY! Thank you for your time to review and answer my question.
Randy
Last edited: