juicethief
Member
- Location
- United States
According to Article 430, fuses can be used for overload protection of motors. So for a 1 HP, 230V, 1? motor with a SF of 1.40 and a nameplate current rating of 7.1A, overload protection would be 8.875 or 9A (7.1 * 1.25). However, if I pull a class j fuse curve it appears that the fuse would take quite some time to open (if at all according to the curve). I know a smaller size fuse would work but the risk of nuisance tripping becomes an issue. Just curious as to whether there was a time limit or range that is acceptable?
Link to TCC from Littelfuse for JTD 6 thru 12A:
http://www.littelfuse.com/data/en/Time_Curve/FCC01-JTD-003(B).V01.PDF
Link to TCC from Littelfuse for JTD 6 thru 12A:
http://www.littelfuse.com/data/en/Time_Curve/FCC01-JTD-003(B).V01.PDF