Re: Fuses keep blowing
Originally posted by mrhanky: The 3 phases only carry 50-60 Amps each.
Not true. It may be true when you take your measurements. But the behavior that you describe tells me that at some point in time, Phase A is drawing more than 100 amps. It may be caused by something that turns on infrequently, and that draws the excessive current when it does turn on. It may be caused by a weak spot in the insulation that comes infrequently into contact with a grounded point.
You didn?t describe the type of facility. Is this a restaurant? Laundromat? Store?
I would start by asking questions, in the hope of discovering an event that is common to all trips. I?d look for something that they did just before the trip. Look for something that they don?t do many times a day, but rather do once every 2-4 days. You might discover, for example, that they have an employee go over the floors with a buffer twice a week, discover that the receptacle used for that buffer is on Phase A, and then discover that the buffer has a ground fault. What you seek to learn is, ?What was happening just before the trip??
Next, I?d have a close look at the 100 panel. Is it labeled? Do you believe the labels? Can you tell what equipment is on Phase A? If so, I?d look into the equipment that does not operate constantly, but rather is operated once or twice a week.