malachi constant
Senior Member
- Location
- Minneapolis
I know a standard circuit breaker is 80% rated - e.g. if you put an 18A load on a 20A breaker it isn't going to work. My co-worker (also a PE) tells me standard fuses are also 80% rated. Is he correct?
Practical example: I have always fused panels and panel feeders assuming a 100%-rated fuse. If I had a panel with 85A of calculated lights and receptacles, I felt comfortable with a 100A fuse. In this example, do I have to use a fuse rated 85A*1.25 -> 110A? And this would only leave the Owner with 110A*0.8 = 88A -> 88A-85A = 3A calculated capacity? Yikes!
FWIW, the fuses I am referring to are Bussmann LPN-RK/LPS-RK and similar.
Thoughts?
Practical example: I have always fused panels and panel feeders assuming a 100%-rated fuse. If I had a panel with 85A of calculated lights and receptacles, I felt comfortable with a 100A fuse. In this example, do I have to use a fuse rated 85A*1.25 -> 110A? And this would only leave the Owner with 110A*0.8 = 88A -> 88A-85A = 3A calculated capacity? Yikes!