Re: Fuses vs Circuit Breakers
On the other hand I feel fuses, dual element time delay, offer the better motor protection, if:
1. The fuses are sized close to the FLA of the motor, say 125%.
2. IEC overloads are used.
Bussman recommends sizing fuses to back up the motor running overload protection. If a motor single phases, a propely sized fuse will open.
The IEC overloads have a differental trip mechanism that on a single phase becomes more sensative to current on the other two.
For an IEC contactor or starter, only fuses offer NEMA type 2 protection. IEC contactors and starters are "delicate" and have to have current limiting fuses ahead of them to protect on a short circuit.
So keep spare fuses, size correctly and you will prevent motor damage.
The maintenance techs at our local paper mills agree that fuses are best. Also Dow Chemical only uses fuses in there MCC's...