Mike01 said:so than you treat fuses just like breakers unless they are rated for 100%.
cschmid said:J fast-acting fuses
R-rated fuses
for motor circuit protection
There are 2 Classes of R fuses. RK-1 & RK-5, The RK-1 are more current limiting. The RK-5 can be sized for most applications at 125% - 150%. The RK-1 Time current cruves are NOT the same as the RK-5, and RK-1 should be sized at 150% to 175% of the FLA of the application. Class J burn warmer, due to the size reduction, and should be sized also to 150%-175% of the FLA. The advantage of the Class J is size. Many manufacturers have Class J Buckets that are doubled up in Switchgear. Said a different way a 2 Class J buckets or panels take up the same space as 1 Class R bucket.What is the difference between class ?R? and class ?J? fuses they are rated 0-600A available 250 or 600V and the size is different the ?J? smaller than the ?R? but is there any difference in their operation they are both labeled as current limiting and sometimes time delay so why one over the other?
It doesn't matter who manufactures the fuses, they all have to fall under the UL standard ie: time current, Current limitation & size, heat rise Umbrella.who are the manufacturers of the fuse(s)?
Most fuses are rated to continously carry rated current either at 100 or 110% at 25 degrees C. Breakers are rated at 40 degrees C. I rarely give advice to rate at 100%. Devices with inrush can not handle this percentage. Purely resistive 115%do you rate fuses the same way or are fused manufactured for 100% continuous load?
All Class R fuses must be labeled ?Current Limiting.? They may be labeled ?Time Delay,? indicating that they meet the optional time-delay test by not opening in less than 10 seconds at 500% of fuse ampere rating[/QUOTE
Per UL248-12 April 14, 2004
8.3 Verification of overload operation
Part 1, Table 4
Test 1 ? 1.35 In
Test 3 ? 2.0 In
Test 5 ? 5.0 In for time-delay fuses only. For 250 V ac fuses rated 30 A or less, the clearing
time may be 8 s minimum.
2.Additionally the CLass J has to hold :135% <60A: open within 1 hr; >60A: open within 2hrFuses with 300kA interrupting ratings are available. Time-delay labeling is available if the fuse meets the UL optional time-delay test requirements of a minimum 10-sec opening time at 500% of fuse current rating.
200% Specific max. opening times by case size
Just my $.02