Hello all,
Project I have is.
I'm wanting to install a step up transformer from 208 3 phase 4 wire feed to a step up transformer, 480 volts 3 phase 4 wire.
Step Up Transformer info: Primary 75kva, 208 3 phase Delta, Secondary is a 460 3 phase Wye.
Doing the math on transformer with it being a 75kva, primary side is 208 x 1.73 = 359.84, 75000 va / 359.84 = 208.4 amps.
Secondary side of trans. 480 x 1.73 = 830.4 , 75000 / 830.4= 90.3.
Ok if I have done my math correct then according to NEC Table 450.3 sizing of Over current protection I have to take my amps times 250% for the primary and 125 % for secondary.
Primary 208.4 x 250% = 521,
Secondary 90.3 x 125% = 112.875.
Am I correct????
If so on the primary side fusing is really high and does my incoming service have to match this?
Or do I have to fuse both primary and secondary sides of the transformer?
Can I just put a disconnect on the primary side and just fuse the Secondary side?
Thanks for all the help.
Gene
Project I have is.
I'm wanting to install a step up transformer from 208 3 phase 4 wire feed to a step up transformer, 480 volts 3 phase 4 wire.
Step Up Transformer info: Primary 75kva, 208 3 phase Delta, Secondary is a 460 3 phase Wye.
Doing the math on transformer with it being a 75kva, primary side is 208 x 1.73 = 359.84, 75000 va / 359.84 = 208.4 amps.
Secondary side of trans. 480 x 1.73 = 830.4 , 75000 / 830.4= 90.3.
Ok if I have done my math correct then according to NEC Table 450.3 sizing of Over current protection I have to take my amps times 250% for the primary and 125 % for secondary.
Primary 208.4 x 250% = 521,
Secondary 90.3 x 125% = 112.875.
Am I correct????
If so on the primary side fusing is really high and does my incoming service have to match this?
Or do I have to fuse both primary and secondary sides of the transformer?
Can I just put a disconnect on the primary side and just fuse the Secondary side?
Thanks for all the help.
Gene