Fusing
ThomasT2025
New Jersey
We have a fuse block that is located behind a panel that covers a built in disconnect on a roof top unit. The fuses are always live but can be shut off from the breaker located in the electrical room (which is stated with a label on the door of the unit). Any comments?
Looks like it's a listed assembly and those fuses were put there by the manufacturer. Anybody who services that equipment should know they are there. Really no different than having to open the cover of a disconnect. I see no problem.
-Hal
-Hal
The fuse block was installed by my company. But I agree with your comment.
They are feeding into the line side of the built in disconnect. The breaker was oversized so it needed to be fused down before the equipment.
The CB is factory installed? It's strange that the factory breaker wouldn't be the correct size. Also I would consider it dangerous to have those fuses energized when the integral breaker is opened. It's not a stretch to think that someone coming along to work on the unit would assume that everything is de-energized once the integral disconnect is opened.
The CB is factory installed but does not do over current protection. The power needed to be fused down before the RTU.