We have a freestanding MDP that feeds mulitple buildings on a site, all under single management. Generator fed, no utility service. One of our electricians produced the sketch below and reportedly has used this setup before in similar applications. Ingoring the fact that the TS is not shown, the idea as he explained it was to take only a 3-wire feeder from the MDP to each out building and treating each outbuilding as and "SDS". At first, It just looked a bit odd. The more I look at it, the more I think it's just flat out wrong.
1. N-G bond in genset and MDP would create a parallel path.
2. There's no bonding between MDP and the out panels. Feeders are are cable and/or nonmetallic conduit.
3. There's a pretty good distance between the MDP and out buildings, which could potentially play havoc with the phase-N and phase-G voltage level at the out buildings.
Seems like, at the very least, it violates 250.32 B requiring an EGC with the supply conductors. I would take a 5-wire feeder (ABC, N, EGC) from MDP to out buildings and connect EGC to GES (rod, water pipe, building steel, concrete-encased in slab) without a N-G bond. Am I nuts?
1. N-G bond in genset and MDP would create a parallel path.
2. There's no bonding between MDP and the out panels. Feeders are are cable and/or nonmetallic conduit.
3. There's a pretty good distance between the MDP and out buildings, which could potentially play havoc with the phase-N and phase-G voltage level at the out buildings.
Seems like, at the very least, it violates 250.32 B requiring an EGC with the supply conductors. I would take a 5-wire feeder (ABC, N, EGC) from MDP to out buildings and connect EGC to GES (rod, water pipe, building steel, concrete-encased in slab) without a N-G bond. Am I nuts?