G E C to neutral on service entrrance sw.

Status
Not open for further replies.

Daja7

Senior Member
I know that the groundinge electrode conductor must terminate on the neutral bar. Question is, we have two Ground rods and #6 bare that goes to the neut. bar. does the cold water conductor also have to go to the neut. bar? We install service entrance rated transfer switches for S.B generators. the switch only has 4 spaces on the neut bar. on for the service entrance neut. one for the panel neut. one for the generator neutal and on for th GEC no room for anything else.
The neut. bar is bonded to the can and a smaller ground bar is in the switch as well. Inspector insisting on both being on Neut bar. I am using the assumption that the cold water ground is supplimental since we have the two rods as the GEC. and would be ok on the ground bar.
 
The Code calls for grounding electrode conductors for a grounded system to connect to the grounded conductor at or ahead of the service neutral buss.
If you water pipe is a grounding electrode the connection must attach to the grounded conductor or to another grounding electrode.
If your water is not an electrode and is simply being bonded, that connection can be to the the service enclosure (see 250.104)

A possible solution would be to install a grounding electrode conductor sized per 250.66 to your ground rod and attach your water
grounding electrode to it by means of a tap or additional connection at the rod.
 