G&W Pad Mounted SF6 Switchgear Controls

Status
Not open for further replies.

W6SJK

Senior Member
Just looking at their catalog.
If you have a 4-way switch for example, with 1 load interrupter switch in, and 3 fault interrupting breaker feeders and pick the basic type 2 control...
Is there one type 2 controller for each feeder breaker? Or does one controller monitor monitor all breakers (with the same trip settings)?

I know, I could wait and ask them on Monday. :)

Thanks!
 
1 per - that's what I expected as reasonable and needed for independent settings but couldn't find anything definitive in online info. It's not like a Basler relay that can cover more than one "way". Thanks
 