Gap at SEC clamp connection

Status
Not open for further replies.

tonype

Senior Member
Location
New Jersey
Is it OK to have a gap at the SEC clamped connection into a panel cabinet? I could stick 2 pens into the opening shown below.
 

Attachments

  • DSCF6047_edited-1.jpg
    DSCF6047_edited-1.jpg
    97.4 KB · Views: 1
Tony what is the yellow stuff inside the connector. Isn't that sealing the hole? Looks like they could have used a smaller connector. Use some duct seal.
 
Looks like an SER connector which is more rounded than an SEU connector. Or as Dennis said it's just the wrong size.
 
Tony what is the yellow stuff inside the connector. Isn't that sealing the hole? Looks like they could have used a smaller connector. Use some duct seal.

Sorry for the delay - had an unexpected item come up in office. The yellow stuff is the hole - that is the wall surface visible
 
I think the connector is likely listed for that size cable, a smaller one could have been used but not necessarily a code requirement to do so.

A plastic bushing could have been used but is not required for cables
 
Is it OK to have a gap at the SEC clamped connection into a panel cabinet? I could stick 2 pens into the opening shown below.

No it is not ok to use the wrong clamp.

312.5 Cabinets, Cutout Boxes, and Meter Socket Enclosures.
Conductors entering enclosures within the scope of
this article shall be protected from abrasion and shall comply
with 312.5(A) through (C).
(A) Openings to Be Closed. Openings through which conductors
enter shall be adequately closed.

314.17 Conductors Entering Boxes, Conduit Bodies, or
Fittings. Conductors entering boxes, conduit bodies, or fittings
shall be protected from abrasion and shall comply
with 314.17(A) through (D).
(A) Openings to Be Closed. Openings through which conductors
enter shall be adequately closed.

110.12(A) Unused Openings. Unused openings, other than those
intended for the operation of equipment, those intended for
mounting purposes, or those permitted as part of the design
for listed equipment, shall be closed to afford protection substantially
equivalent to the wall of the equipment. Where metallic
plugs or plates are used with nonmetallic enclosures,
they shall be recessed at least 6 mm (1⁄4 in.) from the outer
surface of the enclosure.

c2000.JPG
 