Razzap
Member
I will be wiring up a new, unattached 960 square foot garage / shop. I calculated the load on the new unit to be around 65 amps, based on lighting, air compressor, welder, etc... The owner wants a 100 amp feeder installed for future expansion. The garage / shop will be fed from a dwelling with a 100 amp 120 /240 V service. I claim that installing a 100 amp 2-pole breaker in a 100 amp service panel is not practical, or per code. The only article that I can find to support this is Art 220.83(A). The load calcs on the exiisting dwelling are around 45 amps, because most of the appliances and heating loads are gas.
A service upgrade should be done first, since this garage / shop nearly doubles the size of the load. Am I on the right track? Are there any code sections I need to review to verify my concerns?