Can the receptacles for the garage openers be on one circuit or do they have be on separate circuits. I’m wiring big 2 1/2 car garage. I have one circuit for one side another circuit for other side. Can I just come off those circuits to feed each opener.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Can the receptacles for the garage openers be on one circuit or do they have be on separate circuits. I’m wiring big 2 1/2 car garage. I have one circuit for one side another circuit for other side. Can I just come off those circuits to feed each opener.

They can be on the same circuit

210.11(C)(4)

This has nothing to do with the OP's question.
 

kwired

Electron manager
Location
NE Nebraska
Single unit can't exceed 50% of branch circuit rating if "lighting units, cord-and-plug connected utilization equipment not fastened in place, or both, are also supplied". See 210.23(A)(2)
 