Garage door openers

Status
Not open for further replies.

guschash

Senior Member
Location
Ohio
Can the receptacles for the garage openers be on one circuit or do they have be on separate circuits. I’m wiring big 2 1/2 car garage. I have one circuit for one side another circuit for other side. Can I just come off those circuits to feed each opener.
 
Can the receptacles for the garage openers be on one circuit or do they have be on separate circuits. I’m wiring big 2 1/2 car garage. I have one circuit for one side another circuit for other side. Can I just come off those circuits to feed each opener.

They can be on the same circuit

210.11(C)(4)

This has nothing to do with the OP's question.
 
Single unit can't exceed 50% of branch circuit rating if "lighting units, cord-and-plug connected utilization equipment not fastened in place, or both, are also supplied". See 210.23(A)(2)
 