What is the code requirement for garage door openers? 4 bay garage should they be separate or can they be grouped together.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Hmmm, I think it has to do with where the doors are located.

Roger
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
One circuit is fine, unless they're wired to operate simultaneously, in which case you should do a load calculation.
 

McLintock

Senior Member
Location
USA
Occupation
Electrician
What’s the amps on the openers?, what are the size of the doors?, how much will they be used?

In most cases you will be fine, unless they plan to open all 4 a once


“ shoot low boys their riding shetland ponies”
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
I think one circuit would handle them as most are DC motors and don't pull much. But I might be inclined to run two circuits, two doors per circuit, just in case.
 

Beaches EE

Senior Member
Location
NE Florida
Occupation
Electrical Engineer / Facilities Manager
I would design it for 2 separate circuits assumin they are cord & plug so that each can be disconnected separately for servicing. What is the amperage for each unit and do the manufacturer's instructions call for anything specific?
 