Garage "dwelling unit"

Merry Christmas

Steel480

Electrician
Location
USA
Occupation
Electrician
In Massachusetts code says all 15 and 20 amp circuits supplying outlets or devices "in" dwelling units require afci. Would a garage qualify or is this still only GFCI. The NEC definition of dwelling unit no way describes a garage.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
In Massachusetts code says all 15 and 20 amp circuits supplying outlets or devices "in" dwelling units require afci. Would a garage qualify or is this still only GFCI. The NEC definition of dwelling unit no way describes a garage.
There's your answer. No AFCI.
 

Steel480

Electrician
Location
USA
Occupation
Electrician
I think that was thier way of eliminating "similar areas" requirement. Making everything inside the house AFCI.
 