garage frezzer gfci ??
i am working on the garage and my comuster told me that he have 2 fridges and 1 large chest frezzer in the garage and i did check the nec code but i really cant get the point about using the gfci for frezzer but i did recall it they have expemt from that by using single outlet but i want to hear other first before i do anything and the frezzer is full of meat and this garge is being rebulit now it was damage from fire the source of fire started by battrey charger !! it have 1/4 of garage is damaged and now put new roof on now and ready to run the electrical wires soon i know i have a habite to use the gfci all the time but frezzer that part i ran into and i wondering if you have ideas please do pass the word to me
merci marc
stamcon
Re: garage frezzer gfci ??
210-8(a)exception No.2 (99NEC) permits a single receptacle for a single appliance or a duplex receptacle for 2 appliances, located in a dedicated space and not easily moved, to be exempt from the GFCI requirement.
B
bthielen
Guest
In the process of wiring my own home I found that the cost difference between providing GFCI protection to circuits is so minimal that I have decided that when in doubt, add the protection. For example, when using a GFCI receptacle to protect a circuit the cost difference was about $5. Using a GFCI circuit breaker was considerable higher and less practical because the require too much panel space. How long do you think it will be before it is required on all lighting and receptacle circuits?
Bob
racraft
Bob,
The issue with a GFCI on a freezer circuit is not about safety, it is about nuisance tripping of the GFCI caused by the freezer compressor. There are similar issues with GFCIs on other appliance circuits, such as those for refrigerators, washers, sump pumps, etc.
If it were only a safety issue then there would most likely be no discussion.
B
bthielen
Guest
Thanks! I didn't consider the load.
Bob