NEC 2003
210.8(A)(2)Garages, and also accessory buildings that have a floor located at or below grade level not intended as habitable rooms and limited to storage areas, work areas, and areas of similar use
Exception No. 1: Receptacles that are not readily accessible.
(Handbook Commentary)The requirement for GFCI receptacles in garages and sheds, as illustrated in Exhibit 210.10, improves safety for persons using portable hand-held tools, gardening appliances, lawn mowers, string trimmers, snow blowers, and so on, that might be connected to these receptacles, which are often the closest ones available. GFCI protection is also required in garage areas where auto repair work and general workshop electrical tools are used.
(3)Outdoors
(Handbook Commentary) .......Three of these receptacles are considered to be at direct grade level access and must have GFCI protection for personnel.........
Commercial Garages, Repair and Storage
511.12 Ground-Fault Circuit-Interrupter Protection for Personnel.
All 125-volt, single-phase, 15- and 20-ampere receptacles installed in areas where electrical diagnostic equipment, electrical hand tools, or portable lighting equipment are to be used shall have ground-fault circuit-interrupter protection for personnel.
(Handbook Commentary)Ground-fault circuit interrupters (GFCIs) intended to protect personnel from shock hazards are designed to trip when a ground-fault current of 5 milliamperes (plus or minus 1 mA) or greater is detected. The GFCI necessary to comply with the requirement in 511.12 may be either a receptacle-type or a circuit-breaker-type. This requirement applies to receptacles supplying specific types of utilization equipment that will be in use by repair personnel in environments where the floor surface (typically, concrete slabs with direct or indirect earth contact) and the possibility of dampness or even standing water increases the potential for electric shock.