Garage service feed

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
You mention service, is this a service or feeder?
It’s likely a feeder and since 2005 NEC the r requirement has been for as 4 wire feeder, seperate EGC and neutral, s as bc a grounding electrode system, ground rods may not be needed.
 

suemarkp

Senior Member
Location
Kent, WA
Occupation
Retired Engineer
If it has a panel, you need a ground electrode system. Feeder -vs- Service determines whether it is 3 wire or 4 wire supply.
 