Garage service

Status
Not open for further replies.

dog

Member
The question would be for a feeder to subpanel box in a garage from the main general lighting panelbox in a residential service? Does this application require a three or four wire conductor from main with the neutral conductor isolated from grounds at subpanel? The garage will have a ground electrode/ rod to that location(60 amp or maybe 100 amp with a 200 amp main panel box).
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: Garage service

Is the garage detached from the house? You did say it will have its own GES.

Roger

[ August 12, 2003, 09:04 PM: Message edited by: roger ]
 

rb

Member
Location
Tennessee
Re: Garage service

Dog,

You can never go wrong with the four-wire feeder and an isolated neutral. Just bond your equipment grounding conductor to your grounding electrode system.

Before you can use a three-wire feeder and reground the neutral, you must determine if certain conditions are satisfied. If a metallic path exist between the buildings that requires bonding to the electrical system of each building, i.e., metal water pipes, the neutral can't be used for grounding. See 250.32.
 