I have a question about this test question:
What size 120v branch circuit is required for NM cable supplying a 1200va disposal? I came up with with 12.5a requires #14, which is the answer.
My question is about hard wired versus Cord N Plug. Shouldn't a test question state how the disposal is to be wired? Isnt a Cord N Plug disposal required to be 80% of the circuit and #14 would be limited to 12a and a #12 would be required?
What size 120v branch circuit is required for NM cable supplying a 1200va disposal? I came up with with 12.5a requires #14, which is the answer.
My question is about hard wired versus Cord N Plug. Shouldn't a test question state how the disposal is to be wired? Isnt a Cord N Plug disposal required to be 80% of the circuit and #14 would be limited to 12a and a #12 would be required?