mshields
Senior Member
- Location
- Boston, MA
First off, I suspect this is not an NEC driven requirement but if anyone knows the answer, I'd certainly appreciate it.
I've got gas alarm panel in a hospital (happens to be assciated with O2 for a hyperbaric chamber). The plumbing code requires that this alarm panel be annunciated in 2 24/7 locations and that the path of wiring be unique for each. We have always required this to be in rigid conduit of some type most typically EMT. This particular EC is challenging me to prove that this is required. He wants to use Interduct!
Does anyone know if the rigid conduit IS a requirement and if so, where it is documented to be so.
Thanks,
Mike
I've got gas alarm panel in a hospital (happens to be assciated with O2 for a hyperbaric chamber). The plumbing code requires that this alarm panel be annunciated in 2 24/7 locations and that the path of wiring be unique for each. We have always required this to be in rigid conduit of some type most typically EMT. This particular EC is challenging me to prove that this is required. He wants to use Interduct!
Does anyone know if the rigid conduit IS a requirement and if so, where it is documented to be so.
Thanks,
Mike