Our resi guy called today and asked if a laundy room with a gas dryer would still require a 30A outlet for an electric dryer. I called a well respected member of this Forum that is up on dwellings and he agrees that its not required.
After further review and not enough time tonight to pursue this myself, I turn to you for conformation.
This is what I don't quite grasp.
Thanks
After further review and not enough time tonight to pursue this myself, I turn to you for conformation.
This is what I don't quite grasp.
210.11 Branch Circuits Required.
Branch circuits for lighting and for appliances, including motor-operated appliances, shall be provided to supply the loads calculated in accordance with 220.10. In addition, branch circuits shall be provided for specific loads not covered by 220.10 where required elsewhere in this Code and for dwelling unit loads as specified in 210.11(C).
220.10 General.
Branch-circuit loads shall be calculated as shown in 220.12, 220.14, and 220.16.
Required or not? All this appears to me to be calculated if present.220.14 Other Loads ? All Occupancies.
(B) Electric Dryers and Household Electric Cooking Appliances. Load calculations shall be permitted as specified in 220.54 for electric dryers and in 220.55 for electric ranges and other cooking appliances.
Thanks