Natfuelbilll
Senior Member
Is a gas detection system required to be UL listed like a Fire Alarm system package?
I guess we can try this again. Which of the three permitted applications are you attempting to use: 500.7(K)(1) Inadequate Ventilation, (K)(2), Interior of a Building (where the interior does not contain a source) or (K)(3) Interior of a Control Panel?I am wrestling with if the equipment associated with the control of the shutdown criteria and alarm functions need a listing. The analogous equipment in a fire alarm system is the certified fire alarm control panel.
is simply an extension of the "properly documented" requirements in 500.4(A) to establish the basis of a classified location installation.The type of detection equipment, its listing, installation location(s), alarm and shutdown criteria, and calibration frequency shall be documented when combustible gas detectors are used as a protection technique."(bold yours, underline mine)