I have a typical gas station installation. The E/C took advantage of 514.8 Exception 2 and used PVC in his underground runs to the dispensers.
At the service distribution, his GRS conduits from his pumps have the required seal-offs and then enter a metallic wireway. The wireway routes the conductors to the dispenser over-current panel thru a PVC Nipple.
There is an equipment grounding conductor installed in each conduit.
It appears the 501.30 would require bonding of these raceways (and a metallic conduit into the panel) by a means other than double-locknuts, however, with the use of PVC in the underground run this makes no sense to me.
What am I overlooking ?