I have an E/C with a number of years experience doing an installation at a gas station and he is doing something different from the normal here and he has give me a point to ponder on which I need assistance.
For many years E/Cs here have run the power to gasoline dispensers in a totally separate conduit from all other wiring. In this case, the E/C is installing the pump power wiring and wring he identifies as "data" in the same conduit. (His speakers and leakage monitoring data are in other conduits). I questioned this on my first inspection and he pointed out his conduit is terminating in a X-proof J box within the dispenser which does indeed contain corresponding wiring to match his.
My first thought is he is Exception 2 of 725.130(A) in that he is installing all Class 1 wiring methods. The point of termination on the interior of the station is not installed so I am unable to verify the 725.124 portion of the Exception.

Has anyone encounter this and found that his combining of the circuity is acceptable ??
 
(Relocated to NEC Forum to expand views...and hopefuly input)
 