250.104(B) wants gas lines to be bonded,250.52(B)(1) does not want the gas line used as a grounding electrode. So if im reading continuity around the gas meter wouldn't that be a grounding electrode system?
It is almost a word game in that case. You do not connect a GEC sized according to the GEC rules, nor do you count it as a grounding electrode.250.104(B) wants gas lines to be bonded,250.52(B)(1) does not want the gas line used as a grounding electrode. So if im reading continuity around the gas meter wouldn't that be a grounding electrode system?
it was my understanding that the gas company had dielectric unions on the gas meters.But I've had electricans put there continunity tester across the gas meter and we read continunity.So I don't have them bond gas line.Its metal pipe leaving the building
The gas lines generally don't need bonding if there is a gas furnace or some other gas appliance that has electricity hook to it. Now if the gas lines are CSST then that is a different issue and that must be bonded.
I totally agree with Golddigger's points about this. The buried metallic gas supply pipe is in intimate contact with earth and will, electrically, be in continuity with an occupancy's Premises Wiring (System) connection to earth. The gas line meter dielectric union breaks up what would be a parallel continuity path to the gas pipe-->earth-->GES path.it was my understanding that the gas company had dielectric unions on the gas meters.But I've had electricans put there continunity tester across the gas meter and we read continunity.So I don't have them bond gas line.Its metal pipe leaving the building