Technically--- no. I have seen it done but the intersystem bonding unit is not listed for bonding of a gas pipe. I see it is allowed around here but one issue is that there should be three hole left for other systems and once you install the bonding for the csst then you only have 2 left. I would give the authority having jurisdiction a call.
Around here they allow it in most areas.
IMO this should be one of the other systems that needs bonding, and part of the reason we put the IBT there is so that others don't need to gain access to inside electrical enclosures to bond their equipment. Bonding CSST is not covered by NEC, IMO it is not an electrical task either, it is the gas piping installer's task. If he wants to pay an electrician to run his bonding wires, that is up to him, but he is still responsible for installing the gas piping according to it's instructions, which may include bonding instructions.
I agree, and if it's not an NEC required bond, then I see no issue using the ISB, unless the CSST instructions say otherwise.
Right, we would have to know what exactly this bond is for to say how it be made. I have had vague non code required bonding requirements come up in job specs or instructions now and then and I sometimes don't know how to connect it because it's not required in the first placeWell gas metallic gas piping does require bonding according to NEC, but is allowed to be done via EGC of any circuits that may be source for energizing the piping. Just so happens CSST often requires additional bonding requirements per product instructions.
Technically--- no. I have seen it done but the intersystem bonding unit is not listed for bonding of a gas pipe. I see it is allowed around here but one issue is that there should be three hole left for other systems and once you install the bonding for the csst then you only have 2 left. I would give the authority having jurisdiction a call.
Around here they allow it in most areas.
Well gas metallic gas piping does require bonding according to NEC, but is allowed to be done via EGC of any circuits that may be source for energizing the piping. Just so happens CSST often requires additional bonding requirements per product instructions.