Gas Lines in proximity to Electric run

Status
Not open for further replies.

Fordean

Senior Member
Location
New Jersey
Occupation
Electrical Contractor
We have a 400 amp Panelboard 480v Need to install a Step down transformer and run 3 - 1.5 inch Emt Lines to the right. Can go left no room

Problem is the Low side of the gas line comes thru wall and stand off about 4 inches. Going straight up. My only option is to go behind it. Will about a inch or so of clearance. Is their any issue in doing so.
 

Attachments

  • Gas Pipe .png
    Gas Pipe .png
    18.7 KB · Views: 7
No problem if these are on the customer side of the meters.
If on the service side, POCO and gasco may have something to say.
Good luck.

Ron
 