If I have a poly gas line coming to a building where they then transition to a 1" stainless steel pipe for the last 3 feet or so coming out of the ground, does this pipe have to be bonded?
Even if it was in contact with earth the gas line couldn't be an electrode.
250.52(B) Not Permitted for Use as Grounding Electrodes.The following systems and materials shall not be used as grounding electrodes(2) Aluminum
(1) Metal underground gas piping systems
I have often wondered what difference it makes.
These days you have to bond the gas pipe to the GE system if CSST is used. How is that any different than using it as a GE?