gas pipe for raceway??
dorer
Florida
I have a goverment client in Orlando that is requesting the use of an HDPE pipe, designed for high pressure gas lines, for elctrical services to field devices. This client and myself are well aware of UL listed HDPE conduits that are available for this use, but the client seems to be insistant upon the use of the "gas pipe". Can some one direct me to a code section prohibiting this installation????
dorer
Florida
Re: gas pipe for raceway??
Originally posted by bennie:
Who's government? May not go by NEC.
The Orlando-Orange County Expressway Authority is the governing entity and the contract specifications state all materials shall comply with the latest standards of: UL, NFPA (this covers the NEC doesnt it?), NEMA, ANSI, ASTM and IEEE.
bennie
Esteemed Member
There is provisions to allow specific material for specialized purposes. This usually falls under the authority having jurisdiction.
Some projects, under engineering supervision, can be different than spelled out in the NEC.
Unless this can be shown to be a hazard, the government will likely prevail.
dorer
Florida
dorer
Florida
Thanks Bennie. I think I must plan on installing gas lines.
n1ist
Massachusetts
Principal Electrical Engineer
Are there any approved connectors for connecting the gas pipe to electrical boxes?