Got a call from an HVAC guy, gas appliance was replaced and the new appliance has a short 'flex line' connection, the old one had a solid black pipe connection. The remaining black gas line in the building is now not bonded to the electrical other than thru the flex gas line that hits the unit frame.
Inspector is saying the flex line is not approved for grounding.
HVAC is asking for a 'bonding jumper' from the appliance jbox to the black pipe,
There is some other electrical work for me to do there and HVAC guy is asking me to do this while I am there.
Circuit is a 20A so can I just wirenut some #12 green on the equipment ground in the jbox and jump to a standard 'water pipe clamp' on the black pipe? Or do I need a special clamp?
Or do I need to run a #6 from the GEC to the black pipe out at the gas meter?
Thanks all
Happy Friday