RogerB) Other Metal Piping. Where installed in or attached to a building or structure, a metal piping system(s), including gas piping, that is likely to become energized shall be bonded to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor where of sufficient size, or the one or more grounding electrodes used. The bonding jumper(s) shall be sized in accordance with 250.122, using the rating of the circuit that is likely to energize the piping system(s). The equipment grounding conductor for the circuit that is likely to energize the piping shall be permitted to serve as the bonding means. The points of attachment of the bonding jumper(s) shall be accessible.
jayparr said:Does the NEC specifically require metal gas piping to be bonded?
Actually all states should if they are following the NEC as it's worded.Inspectorcliff said:Here in the Colorful State, we allow the second sentence from the end of the quote to do the bonding.
Roger that, Ha, nice picture, how you painted that so quickly is beyond me!!roger said:Actually all states should if they are following the NEC as it's worded.
Roger
roger said:Dennis, why did you assume the OP was talking about CSST?
Roger
Inspectorcliff said:how you painted that so quickly is beyond me!!
fireryan said:So when they use the flexible yellow stuff do you have to put a bonding jumper around it or is it rated for that
Inspectorcliff said:Roger that, Ha, nice picture, how you painted that so quickly is beyond me!!
Dennis Alwon said:I am not really assuming it is but it could be what the op is asking since that is a common question. Many people are very confused on the issue.
which is specifically addressed in 250.104(B)Does the NEC specifically require metal gas piping to be bonded?
Dennis Alwon said:
roger said:But the OP's words were, which is specifically addressed in 250.104(B)
Roger
I don't know what your problem is Dennis, go back and read the thread in order reading the words of the posts and not what you want the posts to say.Dennis Alwon said:Does it really matter. CSST is also a metal gas pipe. I was just making sure the op understood there was a difference but it seems you are not happy with that so......you win-- I won't bring it up
I'm glad someone understands what my question really was.fireryan said:So if I am reading this right as long as the gas pipe is bonded at entry then the flexible yellow gas line is bonded also, but nothing after the yellow flexible line is. such as in larry question in the other post
LarryFine said:I'm glad someone understands what my question really was.