Where does the NEC require all gas lines to be bonded?
The last place I lived had gas only for heat - and the heat was a wall furnace with a standing pilot light. There was NO electrical connection to the gas system anywhere. No fan, no igniter. Gas valve was powered by the thermopile in the pilot flame, and the thermostat worked from a bi-metallic coil.
There's been a lot of confusion over the years regarding 'grounding.' Indeed, the NEC is still confused on this point. Other codes are similarly confused. A better question to ask is "Should I bond the gas line to accomplish "X"? Code will then answer, based on what "X" is.
May I bond to the gas line so it will act as a grounding electrode? No, you may not. NEC says so.
May I bond to the gas line to provide a fault path for a failed gas appliance? NEC says you must.
May I bond the gas line to my grounding electrode, to provide lightning protection? You may - and the plumbing code, fuel gas code, and CSST instructions all say you must when there is CSST present anywhere in the system. (Plese note that "CSST" does NOT include the short flexible whip used to connect appliances).
I know, it's kind of confusing .... whether you are bonding the gas line TO the GEC or whether you are using the gas line AS your grounding electrode depends entirely on which direction you think the electricity will flow. It becomes a word game.