Good Morning,
I have (2) NATURAL GAS Caterpillar generators (G3512) 555KW / 208volts
These Generators will also run on propane, KW drops down to 380KW / 208volts
My problem is they won't run on propane.
(2) 1,000 gallon propane tanks in the ground, vaporizer has been replaced twicedue to being outside and weather conditions etc...
When I switch from natural gas to propane, the (1) incoming 2" pipeline starts to frost up, the 2 engines start to rev up and down.
The (1) 2" pipe comes into the building and branches off to feed thegenerators. Each of the engines has their own factory installed regulator.
There is also regulator out at the vaporizer.
Any direction, advice greatly appreciated.
Thank You