I have a camera install at a new construction gas station. There are indoor cameras (no issues), cameras at the gas pumps, and cameras on light poles around the parking lot.
The inspector said that the cabling needs to be 600V rated since it is inside the light pole with the 110V light circuit (the camera has its own conduit all the way to the concrete base of the lightpole). I am using cat5, and the Belden 7958a I found is $675 a box!
My questions are:
1. Is there an easier/less expensive way to satisfy code?
2. Do I need the same cabling for the cameras mounted under the gas pump canopy (since the area is flammible)? I am running conduit down the surface of the post, with a couple feet of seal-tight up to the camera housing.
3. Could any one point me to the relevant sections in the NEC?
I'd really appreciate any comments/suggestions.