ClayH
Member
- Location
- Lafayette, LA, USA
I had a bit of an argument the other day on the interpretation of the following and was wanting to get others feedback.
I am referencing NFPA 70 - 2014 edition. 501.15 (E)(4) in reference to cable seals in a Class I Division 2 location. NEC allows for type TC-ER cable to be utilized in a CID2 location. The section reference above states that if cable does not have a gas/vapor tight continuous sheath, it shall be sealed at the unclassified boundary in a way that minimizes the passage of gases or vapors.
The question is the terminology that is used defines sheath. Sheath generally relates to a form of armor or welded sheath of a cable, which you will see for MC-HL (Gas/vapor-tight continuous metallic sheath). Or can sheath also be for the outer jacket of a non-armored cable.
Example being, an unarmored TC-ER cable can being utilized in a CID2 location, which is acceptable per NEC. The data sheet of the TC-ER cable defines that it has a gas/vapor tight jacket. (Difference in terminology) Would this cable comply with the requirement of 501.15 (E)(4) for "gas/vapor tight continuous sheath", thus would not require a seal at the boundary b/w CID2 and unclassified location. For arguing sake, there would still be a seal around the cable exterior, but not for the core of the conductor(s).
I am referencing NFPA 70 - 2014 edition. 501.15 (E)(4) in reference to cable seals in a Class I Division 2 location. NEC allows for type TC-ER cable to be utilized in a CID2 location. The section reference above states that if cable does not have a gas/vapor tight continuous sheath, it shall be sealed at the unclassified boundary in a way that minimizes the passage of gases or vapors.
The question is the terminology that is used defines sheath. Sheath generally relates to a form of armor or welded sheath of a cable, which you will see for MC-HL (Gas/vapor-tight continuous metallic sheath). Or can sheath also be for the outer jacket of a non-armored cable.
Example being, an unarmored TC-ER cable can being utilized in a CID2 location, which is acceptable per NEC. The data sheet of the TC-ER cable defines that it has a gas/vapor tight jacket. (Difference in terminology) Would this cable comply with the requirement of 501.15 (E)(4) for "gas/vapor tight continuous sheath", thus would not require a seal at the boundary b/w CID2 and unclassified location. For arguing sake, there would still be a seal around the cable exterior, but not for the core of the conductor(s).