GE 150 amp discolored bus?

Status
Not open for further replies.

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
Attached is something I seen on A GE bus linkage. To me this is bad has anyone else encountered this discoloration. The panel was dry and no other evidence of water damage.
 

Attachments

  • IMG_0175.jpeg
    IMG_0175.jpeg
    968 KB · Views: 71
That is exactly what I thought I have been trying to find a GE panel rep to see if that link is replaceable or if they seen this before.
 
I was wondering if those 2 links were replaceable
What does the bus behind the breakers look like? If too much heat transferred to those as well they probably are no good either, and maybe even heated up components within the main breaker. Time to change the entire panel, and maybe even the branch breakers if heat made it's way to the bus behind them.
 
That's pretty common for GE panels and is typically not a defect.

View attachment 2565906
As I recall, the main kit for GE uses unplated Cu bus, so it discolors if there are any corrosive elements in the air, such as sewer gasses. I used to do a lot of lift station panels, we put a GE load center in one and the consultant rejected the submittal with that comment. We had to put in a Sq. D QO load center because they use a tin plated Cu bus.
 