Oh wow! So that’s typical it did not look right to me. I will try to find a GE rep to explain it
I was wondering if those 2 links were replaceableI think this is one if the few times replacing the guts might make sense
There is a big difference between the panel you posted and the one the op posted. There is rust all over it
what would be an unsafe reading ?Point a thermal camera at it under full load.
What does the bus behind the breakers look like? If too much heat transferred to those as well they probably are no good either, and maybe even heated up components within the main breaker. Time to change the entire panel, and maybe even the branch breakers if heat made it's way to the bus behind them.I was wondering if those 2 links were replaceable
As I recall, the main kit for GE uses unplated Cu bus, so it discolors if there are any corrosive elements in the air, such as sewer gasses. I used to do a lot of lift station panels, we put a GE load center in one and the consultant rejected the submittal with that comment. We had to put in a Sq. D QO load center because they use a tin plated Cu bus.
I should of worded my question what is a safe reading and above that becomes unsafe
That's actually hotter than I thought