LRB
Member
- Location
- Interior Alaska
Good Evening:
A week ago our client smoked the Auto-transformer (actually caught fire) in their 100HP Soft Starter. The cause of the fire was mechanical interlock malfunctioned and 1S contactor only partially opened and auxiliary contacts did not switch positions, therefore the motor ran in the closed transition stage until the transformer self destructed. This is a GE CR 331 NEMA size 4 Auto transformer soft starter. Customer air freighted new transformer. New transformer had no labels or manufacturer name plate nothing.
Customer also has a 50 HP GE auto transformer soft starter which has a Hevy-Duty transformer with connection points labeled H1, H2, H3, 01,02,03, and each phase coil has Tap connections for 50, 65, and 80. New transformer has 3 connection point for each phase coil, 2 at top and 1 at bottom. Applying 120 volts across the various combinations I was able to determine that the 2 at the top were the H and 0 connections and the bottom was 65 % tap. One of the top connections had 4 copper ribbons, and the other connections each had 2 copper ribbons. I labeled the 4 ribbon connector H and the other top top 2 ribbon connector 0, and of course the bottom 2 ribbon connector I labeled 65.
After hook up I opened motor disconnect and monitored voltages through a dry start cycle. I was reading 177 leg to leg, which is 37 % 480. We tried the motor and it does start, however if there is any product left in (hay pellets) the motor will stall. The owners want to run as is until next Wed. and I will be able to make corrections to hook up. I would like the Auto-Transformer pros on this forum to confirm that if I swap the connections that I have labeled H and 0 on each phase I should have ~65 % 480 voltage leg to leg.
I have attached 2 schematic diagrams. The first schematic is from GE website, and the second one was supplied with the Starter. I have done a complete as-built on the cubicle and confirmed that the starter is wired per the schematic supplied by the supplier, however, the write up supplied by the vender does not completely match either schematic, however it does give you an over all sequence of events.
A week ago our client smoked the Auto-transformer (actually caught fire) in their 100HP Soft Starter. The cause of the fire was mechanical interlock malfunctioned and 1S contactor only partially opened and auxiliary contacts did not switch positions, therefore the motor ran in the closed transition stage until the transformer self destructed. This is a GE CR 331 NEMA size 4 Auto transformer soft starter. Customer air freighted new transformer. New transformer had no labels or manufacturer name plate nothing.
Customer also has a 50 HP GE auto transformer soft starter which has a Hevy-Duty transformer with connection points labeled H1, H2, H3, 01,02,03, and each phase coil has Tap connections for 50, 65, and 80. New transformer has 3 connection point for each phase coil, 2 at top and 1 at bottom. Applying 120 volts across the various combinations I was able to determine that the 2 at the top were the H and 0 connections and the bottom was 65 % tap. One of the top connections had 4 copper ribbons, and the other connections each had 2 copper ribbons. I labeled the 4 ribbon connector H and the other top top 2 ribbon connector 0, and of course the bottom 2 ribbon connector I labeled 65.
After hook up I opened motor disconnect and monitored voltages through a dry start cycle. I was reading 177 leg to leg, which is 37 % 480. We tried the motor and it does start, however if there is any product left in (hay pellets) the motor will stall. The owners want to run as is until next Wed. and I will be able to make corrections to hook up. I would like the Auto-Transformer pros on this forum to confirm that if I swap the connections that I have labeled H and 0 on each phase I should have ~65 % 480 voltage leg to leg.
I have attached 2 schematic diagrams. The first schematic is from GE website, and the second one was supplied with the Starter. I have done a complete as-built on the cubicle and confirmed that the starter is wired per the schematic supplied by the supplier, however, the write up supplied by the vender does not completely match either schematic, however it does give you an over all sequence of events.