augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Mar 27, 2023 #1 I'm getting conflicting input on the correct catalog number for a backfed breaker retaining clip for a GE TLM1200RCU Mod 2 Load Center. Anyone familiar with GE that can give the the correct catalog number (local supplier is lost)
brantmacga Señor Member Location Georgia Occupation Former Child Mar 27, 2023 #2 It should be THQLRK1. https://library.industrialsolutions.abb.com/publibrary/checkout/DEJ067?TNR=Installation%20and%20Instruction%7CDEJ067%7CPDF&filename=DEJ067.pdf Here are the other two types for you to review, but I’m pretty sure the K1 is what you need. For 6-8/space load centers https://library.industrialsolutions.abb.com/publibrary/checkout/DEH0004140?TNR=Installation%20and%20Instruction%7CDEH0004140%7CPDF&filename=DEH0004140.pdf This one is for MLO 12-24/space load centers. https://library.industrialsolutions.abb.com/publibrary/checkout/DEH0004141?TNR=Installation%20and%20Instruction%7CDEH0004141%7CPDF&filename=DEH0004141.pdf
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Mar 27, 2023 #3 Thanks... I see why the supplier is confused