S SeniorElectricalEngineer Member Location VA Occupation electrical engineering Oct 14, 2024 #1 Greetings everyone, Last week I was surveying an electrical room and noticed an older GE demand meter referenced in the attached photo. Could you figure out what the max. demand value this meter indicates? Attachments demand meter enlarged.jpg 289.3 KB · Views: 19
Greetings everyone, Last week I was surveying an electrical room and noticed an older GE demand meter referenced in the attached photo. Could you figure out what the max. demand value this meter indicates?
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Oct 14, 2024 #2 It's either 0.34 kw or (2400 x 0.34) 816 kw. I would guess the latter. Big service?
D David Castor Senior Member Location Washington, USA Occupation Electrical Engineer Oct 14, 2024 #3 Looks like about 0.34 x 2400 or 816 kW. Does it seem reasonable? But remember, this is just the maximum since the last time it was reset.
Looks like about 0.34 x 2400 or 816 kW. Does it seem reasonable? But remember, this is just the maximum since the last time it was reset.
S SeniorElectricalEngineer Member Location VA Occupation electrical engineering Oct 14, 2024 #4 816 kW appears to be the correct value. Take a look at the single line diagram. Attachments Screenshot 2024-10-14 184355 existing swgr.jpg 59.2 KB · Views: 12