GE Hydran 201Ti in a Hydran 201Ci-1 Pass-Thru

Status
Not open for further replies.

chedore

GANEX
Location
Quebec, Canada
Occupation
Electromecanical technician, Automation Technician
Hello everyone!

I am currently on a solar panel field trying to figure out the communication between our SCADA and the GE Hydran 201Ci-1. Has anyone here worked with that? This is our campany's first time working with these and we're having a hard time trying to figure everything out. I got all the documentation and the softwares to get myself set up but I am currently lost.

The GE Hydran 201Ti is installed on a 240kv / 35kv transfo.

Thanks in advance for any help !
 

coop3339

Senior Member
Location
NJ
Just took a quick look at it. It looks like it communicates via RS485. The SCADA will need the driver installed to interpret the values.
 

chedore

GANEX
Location
Quebec, Canada
Occupation
Electromecanical technician, Automation Technician
Thanks for your reply @coop3339 !

I actually got everything to work yesterday using RS485 half duplex, plugged into port 21-22-23 of the GE Hydran 201Ci-1
1700262860444.png
The attached picture is when I first got everything to work, after that I cleaned up everything neatly and made a permanent install.

FYI, this was connected RJ45 serial into a SEL-3335 using a SEL-3390S8 interface. Got the modbus map working on my SEL-3335 and all my data was showing up correctly on the SCADA HMI.

Hope this can help someone in the future.

Best regards, Fred.
 