GE panel says use only GE breakers...

Status
Not open for further replies.

zappy

Senior Member
Location
CA.
But I heard on here that Eaton or murray is ok to use in a GE panel. So is it, or is it not ok to install? Thank you.:)
 

peter d

Senior Member
Location
New England
As a general rule of thumb, always match the breaker to the panel. Do not intermix brands, even though the typical 1" stab-in breaker will fit in any 1" panel.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
All of the breaker panels have manufacturer's instructions that say you can only use that brand of breakers in that panel. In general it is UL's position that all manufacturer's instructions are 110.3(B) instructions and must be complied with, except in this case where UL can make more money by "classifying" other breakers to be used in violation of the manufacturer's instructions.
 

zog

Senior Member
Location
Charlotte, NC
I only recommend Zog breakers in Zog panels :)

Of course the manufacturer will say that, after all they want to sell thier breakers as replacements, not anything else.
 

mcclary's electrical

Senior Member
Location
VA
Just because it will fit , doesn't make it right. Around here, if the breaker is not listed for use in the panel it is in, it will not pass inspection
 

ArcNSpark

Member
Location
Coventry, RI
GE's can be tricky. Apparently they're just SLIGHTLY different than a CH or Murray; we used CH breakers in an old GE panel on a remodel. Had maybe 5 callbacks about the oven not working. Apparently the strain of the 8AWG wire bend inside the panel was enough to bring the breakers off of the bus.
 