Hell0 and thanks in advance for any help on this topic!
Currnetly we have a NEMA size 1 GE starter/contactor controlling our sump motor and we are frequently tripping the overload relay thus (almost ) flooding our dike area.
The motor is rated 4A / 1.15FLA @ 40C
CB feed to starter has 5A fuses
the overload heaters are C466A (4.07 to 4.47 A )
I believe everything is sized properly but I am curious about the adjustment dial on the relay heaters that can tripping current. Is this effecting the heater size or something else?
Thanks again!