GEC 4 AWG armor protection

Merry Christmas
Status
Not open for further replies.

Jpflex

Electrician big leagues
Location
Victorville
Occupation
Electrician commercial and residential
#4 AWG Grounding electrode conductor smaller than 6 AWG requiring protection to ground rod

A coworker did this installation but it looks silly and looks as if there may need a red armor cable bushing inside of it at end but a silly looking armor cable connector is connected at end as shown

What is proper way to end armor cable?

Ungrounded conductors are 3/0 so insulated #4 AWG GEC only available was used
 

Attachments

  • IMG_1052.jpeg
    IMG_1052.jpeg
    145 KB · Views: 37

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
Or I should say, multiple manufacturers make it, I'm sure.

Here's an example:


Note the extra little clamp with the two smaller screws. That clamps the cable armor. The ground wire itself is terminated on the big screw in the middle.
 

Jpflex

Electrician big leagues
Location
Victorville
Occupation
Electrician commercial and residential
Or I should say, multiple manufacturers make it, I'm sure.

Here's an example:


Note the extra little clamp with the two smaller screws. That clamps the cable armor. The ground wire itself is terminated on the big screw in the middle.
I’m not sure why this ground clamp doesn’t support this but maybe because it’s designed for GEC not exposed to damage and 6 AWG?
 

Jpflex

Electrician big leagues
Location
Victorville
Occupation
Electrician commercial and residential
Or I should say, multiple manufacturers make it, I'm sure.

Here's an example:


Note the extra little clamp with the two smaller screws. That clamps the cable armor. The ground wire itself is terminated on the big screw in the middle.
So you don’t need a bushing inside of armor as you would MC cable?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
To go with Hal's post the code section is 250.64(E)
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
Which is a violation as done because the flex needs to be bonded to the conductor at each end, same as when sleeving the GEC with EMT or galvanized.

-Hal

GECs are expected to carry unbalanced current, specifically electrical discharges to ground. GECs surrounded by ferrous sleeves are subject to 'choke' effects, and must be bonded to that sleeve at _both_ ends. The install in the photo is IMHO a violation.

-Jon
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
GECs surrounded by ferrous sleeves are subject to 'choke' effects, and must be bonded to that sleeve at _both_ ends. The install in the photo is IMHO a violation.
If the "armor" is ferrous. But if it's aluminum (some FMC, for example), no problem with 250.64(E).

Cheers, Wayne
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I agree that it's most likely 1/2" FMC which is a not permitted method for the protection of a GEC subject to physical damage.
 