#4 AWG Grounding electrode conductor smaller than 6 AWG requiring protection to ground rod

A coworker did this installation but it looks silly and looks as if there may need a red armor cable bushing inside of it at end but a silly looking armor cable connector is connected at end as shown

What is proper way to end armor cable?

Ungrounded conductors are 3/0 so insulated #4 AWG GEC only available was used
 

Attachments

  • IMG_1052.jpeg
    IMG_1052.jpeg
    145 KB · Views: 37
Or I should say, multiple manufacturers make it, I'm sure.

Here's an example:


Note the extra little clamp with the two smaller screws. That clamps the cable armor. The ground wire itself is terminated on the big screw in the middle.
 
Or I should say, multiple manufacturers make it, I'm sure.

Here's an example:


Note the extra little clamp with the two smaller screws. That clamps the cable armor. The ground wire itself is terminated on the big screw in the middle.
I’m not sure why this ground clamp doesn’t support this but maybe because it’s designed for GEC not exposed to damage and 6 AWG?
 
Or I should say, multiple manufacturers make it, I'm sure.

Here's an example:


Note the extra little clamp with the two smaller screws. That clamps the cable armor. The ground wire itself is terminated on the big screw in the middle.
So you don’t need a bushing inside of armor as you would MC cable?
 
To go with Hal's post the code section is 250.64(E)
 
Which is a violation as done because the flex needs to be bonded to the conductor at each end, same as when sleeving the GEC with EMT or galvanized.

-Hal

GECs are expected to carry unbalanced current, specifically electrical discharges to ground. GECs surrounded by ferrous sleeves are subject to 'choke' effects, and must be bonded to that sleeve at _both_ ends. The install in the photo is IMHO a violation.

-Jon
 
GECs surrounded by ferrous sleeves are subject to 'choke' effects, and must be bonded to that sleeve at _both_ ends. The install in the photo is IMHO a violation.
If the "armor" is ferrous. But if it's aluminum (some FMC, for example), no problem with 250.64(E).

Cheers, Wayne
 
I agree that it's most likely 1/2" FMC which is a not permitted method for the protection of a GEC subject to physical damage.
 