Hello electrical gurus
I had a discussion recently with an inspector about the use of FMC over a GEC.
We ran a combination GEC/EGC sized to the GEC spec in EMT out of our solar inverter and bonded it at the entrance to the conduit run and transitioned from the conduit to an LB to FMC for about a 2 foot run inside a closed wall and then into the main service panel. We bonded the FMC connector with a grounding bushing in the box per GEC requirements.
The inspector said the GEC annot be in FMC even under a 6' run. is this correct? I can't find anything in the GEC section or FMC section of the code to disallow it.
thanks
K
I had a discussion recently with an inspector about the use of FMC over a GEC.
We ran a combination GEC/EGC sized to the GEC spec in EMT out of our solar inverter and bonded it at the entrance to the conduit run and transitioned from the conduit to an LB to FMC for about a 2 foot run inside a closed wall and then into the main service panel. We bonded the FMC connector with a grounding bushing in the box per GEC requirements.