Dennis has brought up an interesting (to me) topic in another thread.
310.3 states:
310.3 Stranded Conductors.
Where installed in raceways, conductors of size 8 AWG and larger shall be stranded.
Exception: As permitted or required elsewhere in this Code.
Art 250 discusses bonding when GEC are installed in a metallic raceway and accepts solid or stranded GEC conductors.
If does not specificaly address any limitaions to solid but on the other hand it does exempt them from 310.3
Is it a violation to install a solid #6 GEC (or larger) thru nipples with other conductors ?
Is it a violation to sleeve a #6 (or larger) GEC SOLID in a raceway ?