Questions and guidance please.
1) 250.24(A)(1) states that one of the places the GEC shall be connected can be the neutral bar in panel/disconnect where the service neutral attaches. I understand that.
2) 250.24(A)(4) allows GEC to be on seperate ground bar if there is a jumper between the equipment ground bar and the service neutral bar. I understad that
3) Some disconnects only have enough lugs for the service neutral, the load neutral and the GEC. They have a lug for the Equipment Ground at a remote part of the disconnect
4) 110.3(B) says to follow manufactureres installation instructions.
5) I can see and understand all of the above, But,
So now my question and request for guidance. I have an inspector that requires a jumper from the equipemnt ground bar to the servce neutral bar (in the main or first disconnect panel and not referring to a sub panel). The equipment ground bar is attached according to the manufacturer with screws in ground bar, and main bonding screw/bar, etc all installed. The inspector says it is required to bond these two bars together even when the GEC is attached to the bar with the service neutral. I cannot find anywhere that specifaccly states or describes that. I can see a POSSIBLE instance with a 200 amp disconnect, but the manufacturer doesn't state that when I read the directions. So is a jumper required between these two bars (equipment ground bar and service neutral bar) in the main panel or not, and if it is, please let me know the section number.
Thanks as always,
Kermit
1) 250.24(A)(1) states that one of the places the GEC shall be connected can be the neutral bar in panel/disconnect where the service neutral attaches. I understand that.
2) 250.24(A)(4) allows GEC to be on seperate ground bar if there is a jumper between the equipment ground bar and the service neutral bar. I understad that
3) Some disconnects only have enough lugs for the service neutral, the load neutral and the GEC. They have a lug for the Equipment Ground at a remote part of the disconnect
4) 110.3(B) says to follow manufactureres installation instructions.
5) I can see and understand all of the above, But,
So now my question and request for guidance. I have an inspector that requires a jumper from the equipemnt ground bar to the servce neutral bar (in the main or first disconnect panel and not referring to a sub panel). The equipment ground bar is attached according to the manufacturer with screws in ground bar, and main bonding screw/bar, etc all installed. The inspector says it is required to bond these two bars together even when the GEC is attached to the bar with the service neutral. I cannot find anywhere that specifaccly states or describes that. I can see a POSSIBLE instance with a 200 amp disconnect, but the manufacturer doesn't state that when I read the directions. So is a jumper required between these two bars (equipment ground bar and service neutral bar) in the main panel or not, and if it is, please let me know the section number.
Thanks as always,
Kermit